adccommunitymod (AutomationDirect) asked a question.
DL06 Hi Speed counter
Created Date: May 01,2006
Created By: KeithFutter
**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****
I have an encoder connected to the X1 input of a DL06. The counter is set up in Mode 10 with a single input. The counter counts up to a pre-set number which is loaded from V memory. The counter is self-reset when the count reaches the pre-set number. My problem is that the counter occasionaly resets one pulse before reaching the pre-set count. Count speed is 400 Hz.
Created Date: May 01,2006
Created by: bcarlton
Exactly how are you determining that it resets one pulse before the pre-set count? Can you post your logic?
Created Date: May 02,2006
Created by: KeithFutter
With 'status ' switched on I can watch the incoming pulses to the UDC on the computer. Turning the encoder shaft very slowly, I can see the count increase pulse by pulse until it reaches the number at which it resets (say, 100). Occasionally it resets at 99.
I can send the ladder diag to you, but I can't see how to post it on this board.
Keith
Created Date: May 02,2006
Created by: bcarlton
You can use File - Export - Program to get a text file. As long as the program isn't very long go ahead and post the entire text file by cut-and-paste.
If the 100th pulse occurs after the execution of the counter instruction you may see the count via communication at the end of the scan. Then on the next scan the counter resets. Actually I'm somewhat suprised that you could even see the terminal count.
Created Date: May 03,2006
Created by: bcarlton
Thanks for the program via email, though since you just sent the PRJ file I have no documentation or register values. If it's important for me to see the documentation and values then zip up all the files with the name of your project and email that. If you wish others to help then follow my earlier post, export the project, then cut and paste the text result into a post.
Which value are you looking at for the count, CTA174 or its doubled value in V2002? I'd still be suprised if you do actually catch the final value. Since achieving the final value is used to reset the counter.
You said that the signal is at 400hz. What is the scan time of your program? Since 400hz generates a count every 2.5ms then a scan time of more than that will occasionally see an increase in the accumulated count of more than one count in a scan.
Created Date: May 03,2006
Created by: KeithFutter
Thanks for your reply.
Prog cut and pasted below as you suggest.
The encoder produces 100pprev, each pulse reresenting 2mm. The value in V2000 is the desired distance in mm as set on an Optimate 413 HMI.
The value is then multiplied by 5 and divided by 10 and used as the preset vale in the counter. This way, 200mm distance as set on the Optimate is counted as 100pulses in the counter, which is one rev of the encoder.
Turning the encoder many times with 200mm set, causes the punches to punch at one rev of the encoder shaft - 200mm - with an occasional punch at 198mm.
I beleive the scan time is less than 2mS and the program is very small, so it should be quick.
I could imagine missing pulses if the scan time was too long, but doesn't the HSIO mode ensure that only true incoming pulses are counted, one for one?
Keith
PLC 06
// Rung 1
// Address 0
#BEGIN COMMENT
"Set up hi speed ctr for mode 10 incremental mode "
#END
STR SP0
LD K10
OUT V7633
LD K101
OUT V7634
LD K1006
OUT V7635
LD K107
OUT V7636
LD K1006
OUT V7637
// Rung 2
// Address 11
STR SP1
LDD CTA174
MUL K2
OUTD V2002
LD V2004
OUT V2020
// Rung 3
// Address 17
STR SP1
LD V2000
MUL K5
DIV K10
OUT V2014
// Rung 4
// Address 22
STR SP1
STRN SP1
STR SP0
OR C55
ORN Y15
OR CT174
UDC CT174 V2014
// Rung 5
// Address 30
STR CT174
SETI Y17
// Rung 6
// Address 32
STR Y17
STRE TA250 V2020
OR SP0
OR C55
TMRAF T250 K3
// Rung 7
// Address 40
STRE TA250 V2020
OR SP0
RST Y17
// Rung 8
// Address 44
STR X12
PD C55
// Rung 9
// Address 46
STR X1
PD C50
// Rung 10
// Address 48
STR C50
STR CT5
OR C55
OR SP0
CNT CT5 K2
// Rung 11
// Address 55
STRE CTA5 K1
OUT Y15
// Rung 12
// Address 58
STR X4
PD C110
// Rung 13
// Address 60
STR C110
STR CT10
OR SP0
CNT CT10 K2
// Rung 14
// Address 66
STRE CTA10 K1
OUT Y7
// Rung 15
// Address 69
STR Y7
AND Y17
AND Y15
OUT Y1
// Rung 16
// Address 73
STR X5
PD C120
// Rung 17
// Address 75
STR C120
STR CT20
OR SP0
CNT CT20 K2
// Rung 18
// Address 81
STRE CTA20 K1
OUT Y10
// Rung 19
// Address 84
STR Y10
AND Y17
AND Y15
OUT Y2
// Rung 20
// Address 88
STR X6
PD C130
// Rung 21
// Address 90
STR C130
STR CT30
OR SP0
CNT CT30 K2
// Rung 22
// Address 96
STRE CTA30 K1
OUT Y11
// Rung 23
// Address 99
STR Y11
AND Y17
AND Y15
OUT Y3
// Rung 24
// Address 103
STR X7
PD C140
// Rung 25
// Address 105
STR C140
STR CT40
OR SP0
CNT CT40 K2
// Rung 26
// Address 111
STRE CTA40 K1
OUT Y12
// Rung 27
// Address 114
STR Y12
AND Y17
AND Y15
OUT Y4
// Rung 28
// Address 118
STR X10
PD C150
// Rung 29
// Address 120
STR C150
STR CT50
OR SP0
CNT CT50 K2
// Rung 30
// Address 126
STRE CTA50 K1
OUT Y13
// Rung 31
// Address 129
STR Y13
AND Y17
AND Y15
OUT Y5
// Rung 32
// Address 133
STR X11
PD C160
// Rung 33
// Address 135
STR C160
STR CT60
OR SP0
CNT CT60 K2
// Rung 34
// Address 141
STRE CTA60 K1
OUT Y14
// Rung 35
// Address 144
STR Y14
AND Y17
AND Y15
OUT Y6
// Rung 36
// Address 148
END
// Rung 37
// Address 149
NOP
#BEGIN ELEMENT_DOC
"X1 ", "START Punching ", " ", " "
"X4 ", "Select Pnch1 btn ", " ", " "
"X5 ", "Select Pnch2 btn ", " ", " "
"Y1 ", "Sol valve 1 ", " ", " "
"Y7 ", "Pnch1 selected ", " ", " "
"Y10 ", "Pnch 2 selected ", " ", " "
"Y15 ", "Started ", " ", " "
"Y17 ", "Punch down ", " ", " "
"T250 ", "Punch down timer ", " ", " "
"CT5 ", "Start/stop punch ", " ", " "
"CT174 ", "Length ctr ", " ", " "
"CTA174 ", "Current dist mm ", " ", " "
"V2000 ", "Desired length ", " ", " "
"V2002 ", "Dist travelled ", " ", " "
"V2004 ", "Punch down time ", " ", " "
"V2014 ", "Pre-set lngth ", " ", " "
#END
Created Date: May 03,2006
Created by: bcarlton
If your encoder is a quadrature type you may wish to try mode 20, just in case there is any oscillation enough, especially near the punch point, to cause an extra count.
Created Date: May 01,2006
Created by: KeithFutter
I have an encoder connected to the X1 input of a DL06. The counter is set up in Mode 10 with a single input. The counter counts up to a pre-set number which is loaded from V memory. The counter is self-reset when the count reaches the pre-set number.
My problem is that the counter occasionaly resets one pulse before reaching the pre-set count. Count speed is 400 Hz.