GS2 AC drive unable to set to 15khz on carrier frequency. terrible high pitch noise

Created Date: October 31,2019

Created By: skyboy

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

Hi, I'm a newbie with not much familiarity in automation. My GS2 is causing a serious high pitch noise from My Baldor fan motor. Tried to overrev to 2100rpm(Factory 1750) and she still screams Tech support can figure out how to get the carrier frequency past 12. any other settings in the GS2 module that would restrict me to 12khz


  • adccommunitymod (AutomationDirect)

    Created Date: October 31,2019

    Created by: skyboy

    Hi,

    I'm a newbie with not much familiarity in automation. My GS2 is causing a serious high pitch noise from My Baldor fan motor. Tried to overrev to 2100rpm(Factory 1750) and she still screams

    Tech support can figure out how to get the carrier frequency past 12. any other settings in the GS2 module that would restrict me to 12khz

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: October 31,2019

    Created by: Todd Dice

    Parameter P2.08 should be set to 15 for 15 kHz, according to page 4-21 in the manual.

  • adccommunitymod (AutomationDirect)

    Created Date: October 31,2019

    Created by: MikeN

    The carrier frequency only goes up to 12kHz on GS2 drives. I dont think anyone here where I am has ever thought that the carrier frequency at 12khz is bad at all. If you feel it is excessively loud then perhaps the noise is coming from the fan motor and not the drive?

  • adccommunitymod (AutomationDirect)

    Created Date: October 31,2019

    Created by: skyboy

    Parameter P2.08 should be set to 15 for 15 kHz, according to page 4-21 in the manual.

    Unfortunately the it will not allow 15khz. It shows 1-12. I called support and their GS2’s on hand only got to 12 as well. I may swap motors and see

  • adccommunitymod (AutomationDirect)

    Created Date: November 01,2019

    Created by: Todd Dice

    Unfortunately the it will not allow 15khz. It shows 1-12. I called support and their GS2’s on hand only got to 12 as well. I may swap motors and see

    Then AD needs to fix their manual.

    { "data-align ": "none ", "data-size ": "large ", "data-attachmentid ":126336}

  • adccommunitymod (AutomationDirect)

    Created Date: November 01,2019

    Created by: kewakl

    Check out the voltage requirement for 15KHz(115/230/460V) vs 12KHz(575V)