I'm have a random issue where one of my drives ( 1 of 11) is losing the mod bus settings and reverts to default. I'm not writing any thing other than the freq ref and the run command. I'm using a p3k and the drive is wired into the gsedr100 Ethernet adapter. I am reading motor speed, load, amps, volts, status...


  • adccommunitymod (AutomationDirect)

    Created Date: August 09,2012

    Created by: Do-more PE

    Try cycling power immediately after changing the settings. If that doesn't do it, check your settings in the P3k software in the remote IO set up page.

  • adccommunitymod (AutomationDirect)

    Created Date: August 09,2012

    Created by: sshneider

    I know the word "random " is self-explanatory but, can you think of anything that happens just prior to the loss? I was experiencing the same type of thing with GS Drives, P3K and EDRV Modules and came to find out that whenever you do a Program X-fer or power up the P3K/EDRV will overwrite the programmed settings in the drive. Once I assigned the values in the Hardware config section in Pro Suite, everything was OK. Just a thought..

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: August 08,2012

    Created by: dieseltwitch

    I'm have a random issue where one of my drives ( 1 of 11) is losing the mod bus settings and reverts to default. I'm not writing any thing other than the freq ref and the run command.

    I'm using a p3k and the drive is wired into the gsedr100 Ethernet adapter.

    I am reading motor speed, load, amps, volts, status...