adccommunitymod (AutomationDirect) asked a question.

GS-2 JOG

Created Date: January 28,2008

Created By: twbrock

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

I have set Parameter 3.03 to 09 5.00 to 6.0 I have run contacts to DCM and DI1 to run FWD I have jog contacts to DCM and DI3 to JOG Are these correct. The manual is clear as mud. Thanks TWBrock


  • adccommunitymod (AutomationDirect)

    Created Date: January 29,2008

    Created by: milldrone

    twbrock,

    From the manual page 4-25

    Note: The Jog Command cannot be used when the motor is running. The motor must be

    stopped to initiate this command.

    Also you use only the programmed input (DI3 in your case) do not use the DI1 input also at the same time.

    Vaughn

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: January 29,2008

    Created by: twbrock

    Thanks for the reply

    I thought thats what the manual said but its not real clear

    Thanks again

    Tommy

  • adccommunitymod (AutomationDirect)

    Created Date: January 28,2008

    Created by: twbrock

    I have set Parameter 3.03 to 09

    5.00 to 6.0

    I have run contacts to DCM and DI1 to run FWD

    I have jog contacts to DCM and DI3 to JOG

    Are these correct. The manual is clear as mud.

    Thanks

    TWBrock

    Expand Post