adccommunitymod (AutomationDirect) asked a question.

MB-Gateway & Click Plc

Created Date: November 30,2011

Created By: Gaohinc

**** This post has been imported from our legacy forum. Information in this post may be outdated and links contained in the post may no longer work.****

I have a Click PLC and want to use a PC HMI to monitor it. I 've used AdvancedHMI before which is a free product and is capable of Modbus/TCP. I was wondering if I used a MB-Gateway to interface the PLC to my Ethernet network so I can gain connection to a PC running AdvancedHMI. Does anyone have any experience doing this with this equipment?


  • adccommunitymod (AutomationDirect)

    Created Date: November 30,2011

    Created by: andremholmes

    Use an ethernet to serial converter

  • adccommunitymod (AutomationDirect)

    Created Date: November 30,2011

    Created by: franji1

    The MB Gateway is a relatively new product and is designed for this type of networking.

    Modbus/TCP supports this "gateway " type of addressing where you specify a "router " or "gateway " IP Address, but then embedded in the Modbus request is the specific RTU Unit ID. The MB Gateway "peels off " the TCP Transport Layer then puts it in a serial Modbus packet to that Unit ID out the 485 port. Then the response from the PLC does the opposite operation by reformatting the RTU packet as a valid Modbus/TCP response.

    Make sure you can set the Unit ID (a.k.a. slave ID) in your HMI software when using its Modbus/TCP driver "connection ". This is a number between 1 and 254. It probably defaults to 255 (maybe 0), but you need to set it to the RTU slave ID of your Click.

    You could have multiple Clicks or other Modbus/RTU slaves hanging off your 485 network, and each of those would have to have a different Unit ID (e.g. 1, 2, 3). Then, in your HMI software, you could set up a tag to talk to PLCA Input 16, PLCB Output 12, where PLCA is configured to (for example) Modbus/TCP address 192.168.12.20, Unit ID 1, PLCB is configured for Modbus/TCP address 192.168.12.20, Unit ID 2, where your MB gateway's IP address is 192.168.12.20, for example. Now, your HMI, using Modbus/TCP, can talk to mulltiple PLC's through the MB Gateway.

    Expand Post
  • adccommunitymod (AutomationDirect)

    Created Date: November 30,2011

    Created by: Gaohinc

    I have a Click PLC and want to use a PC HMI to monitor it. I 've used AdvancedHMI before which is a free product and is capable of Modbus/TCP. I was wondering if I used a MB-Gateway to interface the PLC to my Ethernet network so I can gain connection to a PC running AdvancedHMI. Does anyone have any experience doing this with this equipment?