Hello, I am trying to use my new EA3-S3ML with my Click C0-10DRE-D . When I try to set up the panel in CMore Micro as a Click Ethernet Protocol i get an error saying: "Error GUI-182 : This Panel cannot use the ethernet protocol driver. " Has anyone seen this before? I can't imaging that the ethernet port on this is only for programming via the PC and not intended to be used for PLC communication....am I crazy? I am running version 4.21 of the software and the panel has 4.21 firmware. Thanks!
Created Date: November 13,2017
Created by: brian_goTigers
Hello,
I am trying to use my new EA3-S3ML with my Click C0-10DRE-D . When I try to set up the panel in CMore Micro as a Click Ethernet Protocol i get an error saying: "Error GUI-182 : This Panel cannot use the ethernet protocol driver. " Has anyone seen this before? I can't imaging that the ethernet port on this is only for programming via the PC and not intended to be used for PLC communication....am I crazy? I am running version 4.21 of the software and the panel has 4.21 firmware. Thanks!
Created Date: November 13,2017
Created by: BobT65
Sounds like you have selected EA1-S3ML instead of EA3-S3ML